demodude
New Member
Wow...Thanks for the welcoming posts
Hey Guys,
First of all..."Off" thanks for the perfect pdf wiring diagrams.
I'm going to print them up and compare them to my basket wiring.
Friday the 40F is going to a job in the city without ''boom" and "swivel" basket controls. We figure we will operate it from the ground controls which work fine.
THE STORY:
One day the machine started lifting and swivel to the left when ground control was switched to basket controls. "boom and swivel" controls had no affect.
All controls on ground work fine.
We found that if we connected a hot jumper to the "clear" relay in the electrical box behind the hour meter it would close the relay and stop the ghost movement. but still have no boom and swivel at basket.
Though we have checked for obvious loose connections we could have missed something as there is a lot of wiring on the unit.
I pulled the 2 berteu controllers in question and thought about replacing them as the pot on one controller seemed loose. Till I found out they were about 550.00 each. The pots checked out with an ohm meter.
Question:
- Should there be approx 4 to 6 volts at the 2 coil terminal screws when
controllers are in the neutral position? (with no wires attached to these)
- I have a 12 volt reading coming back through one of the coil wires when it
is not connected to the controller unit. I felt that was weird
(controllers in neutral )
-One of the electrical components (resister or diode) seems to get very hot
on boom controller.
I have tried to use some of the previous threads to help me get to this point but welcome you thoughts.
Thanks again everyone.
Hey Guys,
First of all..."Off" thanks for the perfect pdf wiring diagrams.
I'm going to print them up and compare them to my basket wiring.
Friday the 40F is going to a job in the city without ''boom" and "swivel" basket controls. We figure we will operate it from the ground controls which work fine.
THE STORY:
One day the machine started lifting and swivel to the left when ground control was switched to basket controls. "boom and swivel" controls had no affect.
All controls on ground work fine.
We found that if we connected a hot jumper to the "clear" relay in the electrical box behind the hour meter it would close the relay and stop the ghost movement. but still have no boom and swivel at basket.
Though we have checked for obvious loose connections we could have missed something as there is a lot of wiring on the unit.
I pulled the 2 berteu controllers in question and thought about replacing them as the pot on one controller seemed loose. Till I found out they were about 550.00 each. The pots checked out with an ohm meter.
Question:
- Should there be approx 4 to 6 volts at the 2 coil terminal screws when
controllers are in the neutral position? (with no wires attached to these)
- I have a 12 volt reading coming back through one of the coil wires when it
is not connected to the controller unit. I felt that was weird
(controllers in neutral )
-One of the electrical components (resister or diode) seems to get very hot
on boom controller.
I have tried to use some of the previous threads to help me get to this point but welcome you thoughts.
Thanks again everyone.