I’ll start out by saying that I am not an electrician, do not want to teach anyone how to wire anything and don’t want to come across as sounding like I know anything about the subject.
I do want to share some of the wiring ‘mistakes’ that I have recently uncovered with the help of my electrician and I do want to get input from you all as I’ve noticed that there seems to be a lot of good knowledge here. So please, correct me as needed!
A few definitions;
Hot wire – usually black but could also be red or other colors such as when using THHN – The ungrounded conductor.
Neutral – usually white, could be grey, especially if there are multiple voltages present- The grounded conductor. Provides a neutral current return path to the source.
Ground – the earth – like, what we live on.
Grounded – attached to the earth. As the XO terminal on the utility transformer is grounded to the earth.
Ground wire – usually bare copper or aluminum but can be green as with THHN. Creates the Effective Ground Fault Path.
Bonding – Not sure how this is different than grounded, but every metal bit in a system, like work boxes, panel housings, emt pipe, motor housings, etc…, needs to be bonded together.
Circuit Breaker – Provides a means to shut off the flow of electricity in the event of an overload and or a ground fault such as the hot wire coming in contact with any grounded metal part.
Service entrance – The first circuit breaker panel on a property. Power comes from the transformer through the meter to the service entrance.
First one;
This is a sub panel in a customer’s garage. Notice that the green ground screw is still bonding the neutral buss bar to the metal housing and the ground wires and the neutrals are mixed together in the neutral buss bar. This is not correct. The only place that neutrals and grounds are to be mixed is at the service entrance. Mixing neutrals and grounds in a common neutral buss bar at a sub panel creates many parallel neutral current paths returning to the source. That’s what the electrons want to do, return to their point of origin. If there are multiple parallel paths to follow, the electrons will take all available routes, like through the cold water bond and copper plumbing, the housing, and thus the gas line to your boiler, into the earth through a ground rod, etc….. OR… through the worker who inadvertently comes between the neutrals during work on the system. Grounding, ground rods and bonding are NOT to be used for neutral current flow back to the source.
I do want to share some of the wiring ‘mistakes’ that I have recently uncovered with the help of my electrician and I do want to get input from you all as I’ve noticed that there seems to be a lot of good knowledge here. So please, correct me as needed!
A few definitions;
Hot wire – usually black but could also be red or other colors such as when using THHN – The ungrounded conductor.
Neutral – usually white, could be grey, especially if there are multiple voltages present- The grounded conductor. Provides a neutral current return path to the source.
Ground – the earth – like, what we live on.
Grounded – attached to the earth. As the XO terminal on the utility transformer is grounded to the earth.
Ground wire – usually bare copper or aluminum but can be green as with THHN. Creates the Effective Ground Fault Path.
Bonding – Not sure how this is different than grounded, but every metal bit in a system, like work boxes, panel housings, emt pipe, motor housings, etc…, needs to be bonded together.
Circuit Breaker – Provides a means to shut off the flow of electricity in the event of an overload and or a ground fault such as the hot wire coming in contact with any grounded metal part.
Service entrance – The first circuit breaker panel on a property. Power comes from the transformer through the meter to the service entrance.
First one;
This is a sub panel in a customer’s garage. Notice that the green ground screw is still bonding the neutral buss bar to the metal housing and the ground wires and the neutrals are mixed together in the neutral buss bar. This is not correct. The only place that neutrals and grounds are to be mixed is at the service entrance. Mixing neutrals and grounds in a common neutral buss bar at a sub panel creates many parallel neutral current paths returning to the source. That’s what the electrons want to do, return to their point of origin. If there are multiple parallel paths to follow, the electrons will take all available routes, like through the cold water bond and copper plumbing, the housing, and thus the gas line to your boiler, into the earth through a ground rod, etc….. OR… through the worker who inadvertently comes between the neutrals during work on the system. Grounding, ground rods and bonding are NOT to be used for neutral current flow back to the source.