Willie B, that's gonna take me a while to digest...
Thanks for the input!
We bond Neutral (I wish it was called center tap) to Equipment ground & in turn earth for a couple reasons.
A It creates an equipotential plane. Can't get a shock if everything you touch is electrically bonded to everything else.
B It provides a fault current path completing the circuit to transformer. Typically, a fault current path with low impedance will flow sufficient amperage to trip a circuit breaker.
Equipment grounding paths should not carry everyday current. We want all current to flow over intentional paths. If you bond at more than service disconnect some portion of that center tap current will flow over equipment ground paths. Current flowing over equipment grounding paths is dangerous. Connections in equipment ground paths are numerous, they are prone to inadequate connections. I've seen several places where conduit enters a box. They are burned away from current over a high resistance connection.
Electrical inspector tells the cautionary tale of an appliance delivery "installer" putting a three wire cord on a range. This one is real common. He discarded the jumper strap required in the exceptions allowing three conductor circuit cable. Since the strain relief supplied with these cords never fit, he discarded it too. He then shoved the range against the wall pinching the cord against a sharp sheet metal edge. I'm not shure where the sheet metal cut into the cord insulation, but it did.
For a year Mrs. Jones used the range with the frame energized by a "hot" conductor of the cord. With no ground path jumper, no circuit was completed, breaker didn't trip.
After a year, the plumber was there addressing a problem, happened to touch sink & range. He was killed.
Bond neutral to equipment ground only in service disconnect.
Rules are circumstance specific, usually, do not bond in outbuildings. Outbuildings in new installations require both neutral & grounding conductors & driven ground rods, concrete ground or substitute.