• Thank you for visiting HeavyEquipmentForums.com! Our objective is to provide industry professionals a place to gather to exchange questions, answers and ideas. We welcome you to register using the "Register" icon at the top of the page. We'd appreciate any help you can offer in spreading the word of our new site. The more members that join, the bigger resource for all to enjoy. Thank you!

Can this generator be wired 208 3 phase?

Birken Vogt

Charter Member
Joined
Nov 30, 2003
Messages
5,324
Location
Grass Valley, Ca
Probably can but there is not enough info in the listing for me to absolutely say, however it would be very rare to find one that couldn't because 208 is the most common connection.
 

bunkclimber

Well-Known Member
Joined
Jul 29, 2009
Messages
116
Location
MD
you need to find out how many wires the generator end is..most of these are 4wire 1phase & cant be rewired 208/3ph..what you are looking for is a 12wire convertible generator end,can be wired single or three phase
 

Birken Vogt

Charter Member
Joined
Nov 30, 2003
Messages
5,324
Location
Grass Valley, Ca
The pictures of the label say 3 phase and 139 volts per winding, that would indicate that a valid connection would be 277/480, therefore with windings in parallel at 52.8A, it could do 120/208 at 38 kVA.
 