Congrats on passing your inspection Oldandworn. Yeah grounding differs a little bit from state to state. The lug provided on the neutral bar is for bonding a metal nipple. It has been a while since I have done a split meter and panel. Playindirt is right about the power company wouldn't be happy to find a ground wire in there. After having that said, I am reminded that the grounded conductor from the panel bonds the meter base. The earth ground goes to the main panel. I am getting old and worn myself. I forget a lot of things. :Banghead I want to ask you. You said you got a tamper proof outlet. This is in your shop correct? Or barn? I didn't think they are required in a garage or shop or barn? Only in residences. I know that code keeps changing all the time, and me and my co-workers have been talking that eventually they are going to require them for everything except commercial and industrial installations. I am not up to speed on residential code. Maybe it is like that already for all I know. Did you check and find out it was required? Or did you just assume?
Hey thanks ijoker! Just to be clear and placing the metal nipple bonding aside, there are some power companies (not the NEC) that require the ground rod wire to go directly into the meter socket. There is even a small knock out in the bottom of this meter for that wire to pass through and connect to the small lug.
Here is the wording that applies from the 2008 NEC:
406.11 Tamper-Resistant Receptacles in Dwelling
Units. In all areas specified in 210.52, all 125-volt, 15-
and 20-ampere receptacles shall be listed tamper resistant
receptacles.
210.52
(G) Basements, Garages, and Accessory Buildings.
For a one-family dwelling, the following provisions shall apply:
(1) At least one receptacle outlet, in addition to those for
specific equipment, shall be installed in each basement,
in each attached garage, and in each detached garage or
accessory building with electric power.
(2) Where a portion of the basement is finished into one or
more habitable rooms, each separate unfinished portion
shall have a receptacle outlet installed in accordance with this section.
That being stated, I asked the inspector if I needed tamper resistant receptacles in the barn and he said no. He either didn't know or he adjusted the code to what made the most sense to him. I didn't want to fail and have him come back so I installed one just to be sure.