• Thank you for visiting HeavyEquipmentForums.com! Our objective is to provide industry professionals a place to gather to exchange questions, answers and ideas. We welcome you to register using the "Register" icon at the top of the page. We'd appreciate any help you can offer in spreading the word of our new site. The more members that join, the bigger resource for all to enjoy. Thank you!

12" Water Main Leak

xcavate

Well-Known Member
Joined
Jan 30, 2008
Messages
187
Location
Boston,MA
I have a job were another crew installed 400' of 12" ductile water line. The line is leaking out about 8 trash barrels of water in about 30 min.It leaks only from 200psi to 150psi then stops. It holds static pressure. So a pretty sizeable leak. The boss had the leak detectors come out with there high tech gadgets and cant find the leak.

I am left with the task now of trying to repair this thing. We have the leak isloated between two gate valves and there is one mechanical joint in the run. I have already dug up one of the gate vavles and had to put 8 turns on the bolts noone tighten them but that wasnt the leak. Then i dug up the 3 bells behind it and the 45 bend and still no leak. The other gate is located in the middle of the street and I did that tie in. First bell is on the shoulder of the road so it will be tough to dig up.

The leak detector think it might be a split in a length a pipe and thats why he cant pick it up.

I dont want to remove the dirt from the whole main at once due to it might buckle and blow the joints apart. So do I dig the rest of the bells up and hope its a rolled rubber or expose the whole thing a lil at a time and hope i find it. I have a pump on hand to keep at 200 psi while we look for it.

Any suggestions?
 

RollOver Pete

Senior Member
Joined
Mar 5, 2007
Messages
1,510
Location
Indio, Ca
Occupation
Operating Engineer/mechanic
Check out the bells first.
It's much easier than digging up the whole thing.
But pay attention to what you are digging up.
Your leak will travel along the bottom of the main.
When you dig out a bell, a little extra effort digging to the bottom may show you which direction to go.
:cool:
 

xcavate

Well-Known Member
Joined
Jan 30, 2008
Messages
187
Location
Boston,MA
Im just surprised with about 200 gallons leaking out it hasnt surfaced anywhere. The pipe is in sand and we havent even found a spec of water yet.
 

danhoe

Well-Known Member
Joined
Jan 1, 2007
Messages
57
Location
Whitmore Lake, MI
Dig up the mech. joint first, if you already had to tighten up one joint chances are that the other one needs to be snugged up. A rolled rubber on 12" was pushed home with the hoe and the operator would have felt it. How many gallons are you loosing ? how many times have you pumped it up, are there a bunch of dips in the line you might need to work the air out, when you bleed the line out of a hydrant or corp if the water is milky that is a sign of air in your line. pm me if you want I will check in the morning leave me your mobile I will call you and get your problem solved. Dan
 

stumpjumper83

Senior Member
Joined
Jan 13, 2007
Messages
1,979
Location
Port Allegany, pa
Occupation
Movin dirt
I dont know if any companies in your area are simlarly eqquped, but a company named Abel recon, a division of abel construction in mountville, pa. Has a camera crawler that can go down the pipe and have a look see. They may have other technologies that might help too.
 

dayexco

Senior Member
Joined
May 21, 2005
Messages
1,224
Location
south dakota
any hydrants inline? if so, can you isolate it? sometimes the "guts" of a hydrant won't hold pressure, and they'll pee up to the bleeder hole, if you have rock around the hydrant, and never expose themself
 

xcavate

Well-Known Member
Joined
Jan 30, 2008
Messages
187
Location
Boston,MA
Well I have pumped it up about 10 times. The water line is pitched up hill. The main was filled slowly and bleed to the water comes out clear. No hydrants inline and I already dug up the mechanical joint. Its either a split piece of pipe, rolled rubber or some out the gate vavle might be back feeding which I doubt. I have cranked down on the gates and I dont hear any bypass and the correlator didnt pick up anything.

It takes about 8 trash barrels to pump up to 200psi and it all leaks out. So somewhere in between 200 and 300 gallons.

The correlator guy thinks its a spilt peice of pipe. He says if it was a rolled rubber he would have picked up on it.
 

xcavate

Well-Known Member
Joined
Jan 30, 2008
Messages
187
Location
Boston,MA
The second time I pumped it up it held 200psi for 50 min before leaking. The first time and every other time I have lost the amount of water described above. This just stumps me.
 

dayexco

Senior Member
Joined
May 21, 2005
Messages
1,224
Location
south dakota
ductile? my bet's on a rolled/torn gasket. haven't seen many split ductile pipes in my 40 yrs.
 

PipeGuy

Well-Known Member
Joined
Feb 5, 2008
Messages
79
Location
Indiana
does the line pressure always stop at 150 psi? What is the pressure on the main from the city? I would lean towards the MJ fittings to look for the leak. If you have much deflection on your bells look there next, for instance if your water main goes up and down a hill and you just deflected the bells instead of using fittings.
A couple of years ago we had a watermain with a leak and we bact tested it and left the main live. The main was on for about 4 months and the leak never surfaced and it also was in sand.
I still would say you best bet is the MJ fittings then dig the bells.
 

JimBruce42

Senior Member
Joined
Jan 15, 2006
Messages
965
Location
Pennsylvania
Occupation
operator
Sounds familiar... I was on a job this spring, where we had a leak during the pressure test for a new 16" ductile iron run. The guy with the fancy "thingamabobs" came out, went to the far points, and started to narrow it down, but couldn't without getting on the pipe. So we had to dig holes, here, and there eventually we got it to a T-joint and hydrant, but that wasn't it either, went a little further up from it to the joint, nothing, next joint nothing, but the sensor guy was able to say we were within X feet.

Long story short (too late:rolleyes:), turns out that it was a split about 6" long in the pipe itself. The sensor guy said that if it had been a joint or a valve he would have been able to narrow it down in a flash, but a crack in the pipe apparently is a lot trickier to narrow down without digging.

We didn't have any water bubble up either, the pipe run was all shot, so we figure the water was finding a seam in the rock and just following it out.
 

Dwan Hall

Senior Member
Joined
Nov 10, 2004
Messages
1,029
Location
Juneau, Alaska
Occupation
Self Employed
I don't know what I am talking about here but have you ruled out one of your valves not seating? Could go back to the next valve on bath end and test those sections at the same time. may be worth a try.
 

dayexco

Senior Member
Joined
May 21, 2005
Messages
1,224
Location
south dakota
I don't know what I am talking about here but have you ruled out one of your valves not seating? Could go back to the next valve on bath end and test those sections at the same time. may be worth a try.

that is a GREAT idea!....could have existing valve that's bleeding back on you.
 

xcavate

Well-Known Member
Joined
Jan 30, 2008
Messages
187
Location
Boston,MA
Well we think we found the leak..... We have it isolated to the first length of pipe off the street. In the middle of the length is the testing corp. We are thinking maybe the corp was screwed in crossthread.
 

tylermckee

Senior Member
Joined
Jan 9, 2006
Messages
768
Location
washington
Only time we ever get leaks is on the saddle/corp, or on flanged fittings where someone didnt keep the flange faces clean. And we never trust valves, new or old they dont always seal 100% at 200+ PSI.
 

mjd37

New Member
Joined
Jul 11, 2008
Messages
1
Location
washington
I had a similar problem last fall, and it turned out to be the new valves we installed. The submittals were approved for valves with a pressure rating of 150psi. Didn't work too good on a 250psi test. :eek:
 

xcavate

Well-Known Member
Joined
Jan 30, 2008
Messages
187
Location
Boston,MA
Its not the gate valve backfeeding. I have water coming out from under the road. There are no bells under the road. So its either the megalug on the gate or the testing corp which is a direct thread no saddle. It goes from 200 psi to 150 psi in less then 20 min.
 

AtlasRob

Senior Member
Joined
Feb 8, 2008
Messages
1,982
Location
West Sussex UK
Occupation
owner operator
Its not the gate valve backfeeding. I have water coming out from under the road. There are no bells under the road. So its either the megalug on the gate or the testing corp which is a direct thread no saddle. It goes from 200 psi to 150 psi in less then 20 min.

Sorry cant help, but am intrested in your terminology.
Gate valve, Ok no prob.
Bells ? ( push joints on lengths of pipe, male one end, female (bell )on other ?
Megalug ?
Testing Corp ?
 

dayexco

Senior Member
Joined
May 21, 2005
Messages
1,224
Location
south dakota
first pic is of a mega-lug...it's a joint restraining device for mechanical joint pipe

can't find a pic of a corp valve handy....it's just a valve attached to the watermain...for typically a home service connection.
 

Attachments

  • prod_1100.jpg
    prod_1100.jpg